  • Nuisance Alarm LED PM8000 meter
Community Menu
  • Forums
    • By Topic
        • EcoStruxure Building
          • Field Devices Forum
        • EcoStruxure Power & Grid
          • Metering & Power Quality
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
          • Motorabgangstechnik & Antriebstechnik Forum
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Solutions for Motor Management
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
          • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
        • Power Distribution NEMA
          • US Utility Forum
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure Building
        • Field Devices Forum
      • EcoStruxure Power & Grid
        • Metering & Power Quality
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
        • Motorabgangstechnik & Antriebstechnik Forum
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Solutions for Motor Management
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
        • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Power Distribution NEMA
        • US Utility Forum
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • EcoStruxure Power & Grid
          • Backstage Access Resources
        • Industrial Automation
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
          • UK&I Residential and Commercial Electrical Distribution
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
          • Solutions for eMobility
          • Digital Hospital Solutions – UK&I
        • Knowledge Center
          • Industrial Automation How-to videos
          • Digital E-books
          • Success Stories Corner
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
        • Retail
          • Solutions for eMobility
        • Retail
          • Digital Hospital Solutions – UK&I
      • EcoStruxure Power & Grid
        • Backstage Access Resources
      • Industrial Automation
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
        • UK&I Residential and Commercial Electrical Distribution
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
        • Solutions for eMobility
        • Digital Hospital Solutions – UK&I
      • Knowledge Center
        • Industrial Automation How-to videos
        • Digital E-books
        • Success Stories Corner
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
      • Retail
        • Solutions for eMobility
      • Retail
        • Digital Hospital Solutions – UK&I
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
52845members
Join Now
248195posts
Join Now

Nuisance Alarm LED PM8000 meter

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Metering & Power Quality
Solved
michael_franz
Admiral michael_franz
Admiral
‎2017-04-25 07:40 AM
0 Likes
13
303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-04-25 07:40 AM

Nuisance Alarm LED PM8000 meter

We have force all alarms OFF and acknowledged all alarms current and historical on a PM8000 meter with a remote display and yet the RED LED on the meter face refuses to extinguish.  It is solid red.

We performed the same steps on three meters at our building and were able to get the LED to go out.

The one at the customer site will not go out.

Any idea?

Thanks,

Michael

Tags (4)
  • Tags:
  • led
  • nuisance alarm
  • pm8000
  • remote display
Share

Accepted Solutions
michael_franz
Admiral michael_franz
Admiral
‎2017-05-09 12:35 PM
1 Like
8
165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-05-09 12:35 PM

Re: Nuisance Alarm LED PM8000 meter

Brian:

We disable and cleared all alarms.  The LED persisted.  We did swap out the display and

the issue followed the display to another meter.  The display itself is the problem and

not the meter.

Working on an RMA from Schneider so they can replace the unit and get this on into the

lab for testing.

Thanks,

Michael

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
13 Replies 13
Eddic
Lieutenant | EcoXpert Master Eddic Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
‎2017-04-25 07:50 AM
1 Like
2
165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-04-25 07:50 AM

Re: Nuisance Alarm LED PM8000 meter

Is there any remains activated alarm in the current alarm list ?

In my experience, if there has any alarm still activate, the led will stay at solid RED

Share
michael_franz
Admiral michael_franz
Admiral
‎2017-04-25 07:54 AM
0 Likes
0
165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-04-25 07:54 AM

Re: Nuisance Alarm LED PM8000 meter

All alarms are force OFF and everything acknowledged.

Share
BrianB
Lieutenant BrianB Lieutenant
Lieutenant
‎2017-05-09 10:42 AM
0 Likes
9
165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-05-09 10:42 AM

Re: Nuisance Alarm LED PM8000 meter

Hi there Michael.

Could you please open a tech support case for this. Tech support will log into the meter and issue some factory commands which checks the status of the alarms through firmware. 

Another test that would be of benefit is to swap a RMD from a unit that has the LED off with the one that has it on.

Out of curiosity, if an alarm is triggered, then cleared (so the alarms are in the historical section, without being acknowledged) the light should be steady on, does it go to this state, or does it go out.

Either way lets get a customer support case opened up with the above information, and I will assist with getting this resolved.

Brian

Share
michael_franz
Admiral michael_franz
Admiral
‎2017-05-09 12:35 PM
1 Like
8
166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-05-09 12:35 PM

Re: Nuisance Alarm LED PM8000 meter

Brian:

We disable and cleared all alarms.  The LED persisted.  We did swap out the display and

the issue followed the display to another meter.  The display itself is the problem and

not the meter.

Working on an RMA from Schneider so they can replace the unit and get this on into the

lab for testing.

Thanks,

Michael

See Answer In Context

Share
BrianB
Lieutenant BrianB Lieutenant
Lieutenant
‎2017-05-09 12:51 PM
0 Likes
7
165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-05-09 12:51 PM

Re: Nuisance Alarm LED PM8000 meter

Ah yes, I was working on that with Steven, I look forward to seeing the unit here at our facility.

Brian

Share
michael_franz
Admiral michael_franz
Admiral
‎2017-05-11 12:13 PM
0 Likes
6
165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-05-11 12:13 PM

Re: Nuisance Alarm LED PM8000 meter

Brian:

We are working on getting an RMA with Graybar for the display...oh poodles

Share
BrianB
Lieutenant BrianB Lieutenant
Lieutenant
‎2017-05-11 12:23 PM
2 Likes
5
165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-05-11 12:23 PM

Re: Nuisance Alarm LED PM8000 meter

Whatever your normal RMA procedure is is fine.  I m pretty sure it will cross my desk at some point.

When they give you an RMA number let me know and I will put some notes in

Share
michael_franz
Admiral michael_franz
Admiral
‎2017-06-30 12:07 PM
0 Likes
4
165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-06-30 12:07 PM

Re: Nuisance Alarm LED PM8000 meter

Brian:

We did the RMA.  Somehow it came in for the whole meter and not just the display.  Only the display had a problem.  Just looked on the Graybar desk.  The box is still here.  Hope it gets back to your team soon.

Michael

Share
BrianB
Lieutenant BrianB Lieutenant
Lieutenant
‎2017-06-30 01:06 PM
1 Like
3
165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-06-30 01:06 PM

Re: Nuisance Alarm LED PM8000 meter

I was thinking about this the other day.  Looking forward to seeing it, a most interesting puzzle.

Share
michael_franz
Admiral michael_franz
Admiral
‎2017-06-30 01:09 PM
0 Likes
0
165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-06-30 01:09 PM

Re: Nuisance Alarm LED PM8000 meter

I emailed the Graybar person who is handling this and hope to hear back soon.

Likely the display just has a bad IC feeding the LED or a bad solder joint on the

board somewhere.

thank,

Michael.

Share
michael_franz
Admiral michael_franz
Admiral
‎2017-07-10 10:45 AM
0 Likes
0
165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-07-10 10:45 AM

Re: Nuisance Alarm LED PM8000 meter

Brian:

Graybar promised it would be shipped out last Friday.  Should be home soon.

Thanks,

Michael

Share
michael_franz
Admiral michael_franz
Admiral
‎2017-07-10 10:46 AM
0 Likes
0
165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-07-10 10:46 AM

Re: Nuisance Alarm LED PM8000 meter

It is just on no matter what we do...even with all alarms disabled and acknowledged it is on.

Share
michael_franz
Admiral michael_franz
Admiral
‎2017-07-17 05:55 AM
0 Likes
0
165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2017-07-17 05:55 AM

Re: Nuisance Alarm LED PM8000 meter

Tracking info on meter...

Attachments
Share
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
142
Robert_Lee
Captain Robert_Lee Captain
56
Ramasamy_N
Commander Ramasamy_N Commander
40
DanL
Lt. Commander DanL Lt. Commander
30
Nedjma
Nedjma Community Alumni (Retired)
24
Daniel_Brandao
Lt. Commander Daniel_Brandao Lt. Commander
17
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2021, Schneider Electric