Dear Group,
need help o explain the following.
How this can be configured in the ION? Since 4,294,967 < 8,216,743.93.
Link copied. Please paste this link to share this article on your social media post.
we got a direction from Anup Surendran Chozhiyattel Thiyyath <anup.surendran@se.com> , to configure the modbus mapping. meaning , to create new 4 registers (4*16 bit = 64 bit).
in this way , the ION will store the values "as is" in these new registers.
by this way, we can take the full value of the reading, in Watt resolution.
the max range shall be 2^64 =18446744073709551616 W = 18,446,744,073,709 MW. that is 2M times grater than the current value.
we shall try this solution and update the case.
Link copied. Please paste this link to share this article on your social media post.
You mean this register address 40232 ?
Label Address Module no. Module label No. of registers Format Scaling Scaling Enable
kWh rec 40232 9 kWh/kVArh 2 INT32 1/1000 No
Use ION Setup connect to meter change to Advance option select Modbus Slave module go to module No. 9 then configure it.
Hope this may help.
Link copied. Please paste this link to share this article on your social media post.
Hello,
The scaling of the register also needs to be taken into account, 1/1000 means that the value send via modbus will be 1000 times as large as the value in the register so when the modbus value is divided by 1000, the end result is 3 decimal points. With the default scaling and configuration, the maximum MWH to be sent = ((2^32 )/1000 )/1000) = 4,294.967296. There are a few options. A) link MWH to the modbus slave module, B) Reduce the scaling.
Link copied. Please paste this link to share this article on your social media post.
Dear Yut,
thanks for the reply.
so, what is the right scaling to choose in ION step up? in order can show bigger values ? (like the
thanks
Link copied. Please paste this link to share this article on your social media post.
i agree with you about the maximum value in MWH it can reach with 2 registers.
but the meter now shows this value in its display " 8x10^6 MWH "and still can increase.
Link copied. Please paste this link to share this article on your social media post.
Note that inside the meter, the module in question is Float 64 bit number, only the modbus register is 32 bit integer.
Link copied. Please paste this link to share this article on your social media post.
we got a direction from Anup Surendran Chozhiyattel Thiyyath <anup.surendran@se.com> , to configure the modbus mapping. meaning , to create new 4 registers (4*16 bit = 64 bit).
in this way , the ION will store the values "as is" in these new registers.
by this way, we can take the full value of the reading, in Watt resolution.
the max range shall be 2^64 =18446744073709551616 W = 18,446,744,073,709 MW. that is 2M times grater than the current value.
we shall try this solution and update the case.
Link copied. Please paste this link to share this article on your social media post.
Hi @sesa82148_bridg,
Did you find your answer to the replies above?
If yes, please click on "Accept as Solution" at the bottom right corner of the answer which helps you.
You can also thank the members who tried to help you by liking their comments!
Have a nice day.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.