Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello Yut,
Looking at the QuickION.cfg file in C:\Program Files (x86)\Schneider Electric\ION Setup\Tables\XXX\YYYY where XXX is the model and YYYY the display options, I see that the ION8800 meters do not include the MV-90 report option.
Likely you will need to log a case with Technical support (se.com-> support -> contact support) to have this tracked.
It may be possible to modify the .cfg file. A) Make a backup of the .cfg file and store in a safe location like desktop B) Edit the file with a text editor and replace the reports section with the text below.
Please note I do not have an ION8800 to test with right now.
Charles
[Reports]
TabCount=1
Tab1=Meter Info
Tab1Type=2
Tab1Text=Allows you to view/store meter information.
Tab1Buttons=1
Tab1Button1Label=Display
Tab1Button1=0,8
Tab1Registers=7
Tab1Reg1=10,1,0x0F80,Revenue Log
Tab1Reg1Text=This shows the meter revenue log information.
Tab1Reg2=10,1,0x0F89,EnergyDemand Log
Tab1Reg2Text=This shows the meter energydemand log information.
Tab1Reg3=10,1,0x1000,Event Log
Tab1Reg3Text=This shows the meter event information.
Tab1Reg4=10,1,0x3,Meter Configuration
Tab1Reg4Text=This reports the meter configuration information.
Tab1Reg5=10,1,0x4,Configuration Comparison
Tab1Reg5Text=This reports the differences between a stored meter configuration file and the present meter configuration.
Tab1Reg6=10,1,0x2,Template Comparison
Tab1Reg6Text=This reports the differences between a stored template and the meter template.
Tab1Reg7=10,1,0x5,MV-90 Report
Tab1Reg7Text=This reports information useful for MV-90 and allows saving info to a MV-90 Master file for importing.
Link copied. Please paste this link to share this article on your social media post.
Hello Yut,
Looking at the QuickION.cfg file in C:\Program Files (x86)\Schneider Electric\ION Setup\Tables\XXX\YYYY where XXX is the model and YYYY the display options, I see that the ION8800 meters do not include the MV-90 report option.
Likely you will need to log a case with Technical support (se.com-> support -> contact support) to have this tracked.
It may be possible to modify the .cfg file. A) Make a backup of the .cfg file and store in a safe location like desktop B) Edit the file with a text editor and replace the reports section with the text below.
Please note I do not have an ION8800 to test with right now.
Charles
[Reports]
TabCount=1
Tab1=Meter Info
Tab1Type=2
Tab1Text=Allows you to view/store meter information.
Tab1Buttons=1
Tab1Button1Label=Display
Tab1Button1=0,8
Tab1Registers=7
Tab1Reg1=10,1,0x0F80,Revenue Log
Tab1Reg1Text=This shows the meter revenue log information.
Tab1Reg2=10,1,0x0F89,EnergyDemand Log
Tab1Reg2Text=This shows the meter energydemand log information.
Tab1Reg3=10,1,0x1000,Event Log
Tab1Reg3Text=This shows the meter event information.
Tab1Reg4=10,1,0x3,Meter Configuration
Tab1Reg4Text=This reports the meter configuration information.
Tab1Reg5=10,1,0x4,Configuration Comparison
Tab1Reg5Text=This reports the differences between a stored meter configuration file and the present meter configuration.
Tab1Reg6=10,1,0x2,Template Comparison
Tab1Reg6Text=This reports the differences between a stored template and the meter template.
Tab1Reg7=10,1,0x5,MV-90 Report
Tab1Reg7Text=This reports information useful for MV-90 and allows saving info to a MV-90 Master file for importing.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.