I had this question regarding connector kit for METSEPM89M2600, but maybe I have placed my question in wrong forum.
Sometimes it happens that Phoenix connectors for this module are lost in factory.
So the question is: maybe there is an ordering number for connector kit? or maybe I can ask people from procurement department, maybe they have Phoenix Contact reference numbers and I can order connectors from local Phoenix Contact. At this time I have uncertainty whether the connectors are in US imperial dimensions or metric dimensions: 5.08 mm contact pitch or 5 mm pitch. On small connector it does not matter, but on bigger one I may have a problem.
Boris Grinac
Prague
Link copied. Please paste this link to share this article on your social media post.
Hello Boris,
All of the PM8k, ION9k, ION74xx platform use either 5.08mm or 7.62mm pitch, Phoenix Combicon plugable connectors.
For METSEPM89M2600 specifically, here are the three connector parts:
Description: Schneider Internal Part Number; Phoenix Contact part number
Digital Out: NHA3151902; 1758830
Digital In: NHA3151802; 1710120
Digital Whetting: NHA3151702; 1758856
Note that the Schneider parts are custom marked with symbols; where as the Phoenix parts are generic (no marking).
Cheers!
Stewart
Link copied. Please paste this link to share this article on your social media post.
Hello Boris,
All of the PM8k, ION9k, ION74xx platform use either 5.08mm or 7.62mm pitch, Phoenix Combicon plugable connectors.
For METSEPM89M2600 specifically, here are the three connector parts:
Description: Schneider Internal Part Number; Phoenix Contact part number
Digital Out: NHA3151902; 1758830
Digital In: NHA3151802; 1710120
Digital Whetting: NHA3151702; 1758856
Note that the Schneider parts are custom marked with symbols; where as the Phoenix parts are generic (no marking).
Cheers!
Stewart