Is there a 'tool' that determines how many days of onboard logging could be achieved, based on parameters defining the logs you wish to set up on the device?
Link copied. Please paste this link to share this article on your social media post.
We have this spreadsheet for PM556x: https://schneider-electric.box.com/s/olhslwkgiwy21i8kr6mz
On the basic range this is really the only meter that has configurable logging capability.
Link copied. Please paste this link to share this article on your social media post.
Hi Dan,
How's the going over there?
I made a spreadsheet for the PM800, but it is not validated. Be aware, that in PM800 you are not only limited by the memory. You have also a limitation by the number of entries (max. 5000). You can find the spreadsheet (without guarantee) in the attachment.
Best Regards
Daniel