Sign In Help
Schneider Electric
HelpLogin / Register

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Communities
  • :
  • EcoStruxure Power & Grid
  • :
  • Metering & Power Quality
  • :
  • ION8650 /8800 IEC 61850 report control block
Community Menu
  • Forums
    • By Topic
        • EcoStruxure Building
          • Field Devices Forum
        • EcoStruxure Power & Grid
          • Metering & Power Quality
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Automation Forum
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
          • Motorabgangstechnik & Antriebstechnik Forum
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Solutions for Motor Management
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
          • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
        • Power Distribution NEMA
          • US Utility Forum
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure Building
        • Field Devices Forum
      • EcoStruxure Power & Grid
        • Metering & Power Quality
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Automation Forum
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
        • Motorabgangstechnik & Antriebstechnik Forum
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Solutions for Motor Management
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
        • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Power Distribution NEMA
        • US Utility Forum
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • EcoStruxure Power & Grid
          • Backstage Access Resources
        • Industrial Automation
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
          • UK&I Residential and Commercial Electrical Distribution
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
          • Solutions for eMobility
          • Digital Hospital Solutions – UK&I
        • Knowledge Center
          • Industrial Automation How-to videos
          • Digital E-books
          • Success Stories Corner
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
        • Retail
          • Solutions for eMobility
        • Retail
          • Digital Hospital Solutions – UK&I
      • EcoStruxure Power & Grid
        • Backstage Access Resources
      • Industrial Automation
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
        • UK&I Residential and Commercial Electrical Distribution
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
        • Solutions for eMobility
        • Digital Hospital Solutions – UK&I
      • Knowledge Center
        • Industrial Automation How-to videos
        • Digital E-books
        • Success Stories Corner
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
      • Retail
        • Solutions for eMobility
      • Retail
        • Digital Hospital Solutions – UK&I
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Register Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
53224members
248688posts

ION8650 /8800 IEC 61850 report control block

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Metering & Power Quality
Solved
Yut
Captain Yut
Captain
‎2021-03-02 12:28 AM
0 Likes
8
210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-03-02 12:28 AM

ION8650 /8800 IEC 61850 report control block

We try to connect the ION meter to SCADA/HMI (ION8800/ION8650) using IEC 61850.

The SCADA use the CID file from meter as reference urcbMMXU01 to urcbMMXU04 but the meter send them with 01 at end. We try to configure the OptFields seqNum to false but when the CID file was upload back to meter we got Invalid CID file.

 

CID file

<ReportControl bufTime="1000" buffered="false" confRev="1" datSet="MMXU" desc="Unbuffered Measurements Report" indexed="false" intgPd="0" name="urcbMMXU01" rptID="urcbMMXU1">
<Private type="SchneiderElectric-SFT-IsPredefined"/>
<TrgOps dchg="true" dupd="false" period="true" qchg="true"/>
<OptFields configRef="true" dataRef="false" dataSet="true" reasonCode="true" seqNum="true" timeStamp="true"/>
</ReportControl>

 

 

Screen shot from scanner the 01 was added monitor from Wireshark also show that the meter add 01. Please advice how the 01 would be eliminated.

 

IEC6185urbc1.png

  • PowerLogic
    PowerLogic ION8650 series
View products (1)
Labels
  • ION Setup
Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard
‎2021-03-02 10:16 AM
1 Like
5
197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-03-02 10:16 AM

Re: ION8650 /8800 IEC 61850 report control block

Hello Yut,

 

I did a bit of investigation and can confirm that the 01 at the end of the name is due to feature described by the IEC 61850 standard, called indexing*. This can be a little misleading as the meter only supports a single subscription to each report but supports 4 "copies" of the report, each with a different name.

 

* IEC 61850-7-2 Edition 2, Communication networks and systems for power utility automation – Part 7-2: Basic information and
communication structure – Abstract communication service interface(ACSI), 2010.

https://cms-cdn.selinc.com/assets/Literature/Publications/Technical%20Papers/6912_LessonsLearned_BW_... page 4 for more information if desired.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
8 Replies 8
Sanjeet_Sahota
Lieutenant Sanjeet_Sahota Lieutenant
Lieutenant
‎2021-03-02 08:54 AM
0 Likes
1
202
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-03-02 08:54 AM

Re: ION8650 /8800 IEC 61850 report control block

Hi Yut,

 

Can you share which firmware version you are using?


Regards,

Sanjeet

Tags (1)
  • Tags:
  • english
Share
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard
‎2021-03-02 10:16 AM
1 Like
5
198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-03-02 10:16 AM

Re: ION8650 /8800 IEC 61850 report control block

Hello Yut,

 

I did a bit of investigation and can confirm that the 01 at the end of the name is due to feature described by the IEC 61850 standard, called indexing*. This can be a little misleading as the meter only supports a single subscription to each report but supports 4 "copies" of the report, each with a different name.

 

* IEC 61850-7-2 Edition 2, Communication networks and systems for power utility automation – Part 7-2: Basic information and
communication structure – Abstract communication service interface(ACSI), 2010.

https://cms-cdn.selinc.com/assets/Literature/Publications/Technical%20Papers/6912_LessonsLearned_BW_... page 4 for more information if desired.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Yut
Captain Yut
Captain
‎2021-03-02 05:26 PM
0 Likes
0
189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-03-02 05:26 PM

Re: ION8650 /8800 IEC 61850 report control block

for the ION8800 V370

ION8650 004.031.001

Tags (1)
  • Tags:
  • english
Share
Reply
Yut
Captain Yut
Captain
‎2021-03-02 05:29 PM
0 Likes
0
188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-03-02 05:29 PM

Re: ION8650 /8800 IEC 61850 report control block

The index option in the CET850 was unchecked.

 

We will do further experiment on both side.

Tags (1)
  • Tags:
  • english
Share
Reply
Yut
Captain Yut
Captain
‎2021-03-02 11:46 PM
0 Likes
3
185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-03-02 11:46 PM

Re: ION8650 /8800 IEC 61850 report control block

OK I got it. The RptEna is False. So I have to study CET850 how to set it to True.

RptEna.png

Tags (1)
  • Tags:
  • english
Share
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard
‎2021-03-03 05:12 AM
0 Likes
2
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-03-03 05:12 AM

Re: ION8650 /8800 IEC 61850 report control block

RptEna  is true when IEC 61850 client has successfully subscribed to the report on the meter. It is not a variable that can be "set" from outside the meter.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Share
Reply
Yut
Captain Yut
Captain
‎2021-03-04 12:31 AM
0 Likes
1
175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-03-04 12:31 AM

Re: ION8650 /8800 IEC 61850 report control block

Any suggestion to let the customer be able to get report with their SCADA/HMI ?

Tags (1)
  • Tags:
  • english
Share
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard
‎2021-03-04 08:40 AM
0 Likes
0
173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-03-04 08:40 AM

Re: ION8650 /8800 IEC 61850 report control block

Have the SCADA/HMI use indexing as defined in the standard?!?

 

I am guessing the name difference is why the client is not getting data from the meter.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Share
Reply
Related Products
PowerLogic
PowerLogic ION8650 series
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
144
Robert_Lee
Captain Robert_Lee Captain
56
Ramasamy_N
Commander Ramasamy_N Commander
41
DanL
Lt. Commander DanL Lt. Commander
31
Nedjma
Nedjma Community Alumni (Retired)
24
Daniel_Brandao
Lt. Commander Daniel_Brandao Lt. Commander
17
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2021, Schneider Electric