Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Posted: 2018-09-07 06:03 PM . Last Modified: 2020-12-02 03:31 AM
Link copied. Please paste this link to share this article on your social media post.
Under what conditions, the voltage 5th harmonic will increase to 300%
Link copied. Please paste this link to share this article on your social media post.
Hi Gibson,
For the first 3 screenshots, the y-axis is in magnitude Volts, not % of nominal. The H5 is shown around 250~300V. If the fundamental frequency voltage is 22.8kV, then a THDv of 1~2% makes sense.
As for the 4th screenshot, I suspect it is the same issue. Is it a custom screen in PSO? We would need to verify the measurement sources.
Link copied. Please paste this link to share this article on your social media post.
Hi Gibson,
For the first 3 screenshots, the y-axis is in magnitude Volts, not % of nominal. The H5 is shown around 250~300V. If the fundamental frequency voltage is 22.8kV, then a THDv of 1~2% makes sense.
As for the 4th screenshot, I suspect it is the same issue. Is it a custom screen in PSO? We would need to verify the measurement sources.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.