Hello Everyone!
Recently I had some questions of customers about ION7400, the most common question is: when the memory log (512 Mb) of this meter will be available to use all its storage capacity?
ION7400 Datasheet said only 10 Mb is available for Framework, what about the other 502 Mb?
Will be there a new firmware to enable all 512 Mb for ION7400 meter?
Best Regards
Farid Yauri
Link copied. Please paste this link to share this article on your social media post.
I check my unit ION7400 found only 10MB
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
We have an ongoing project at this moment to "unlock" the memory on PM8000 / ION7400 meters. This will be done by a firmware upgrade and the total logging memory available will be 350 MB (the rest is used by the meter for other functions). This new firmware is scheduled to be available in November 2017.
Link copied. Please paste this link to share this article on your social media post.
Hi Daniel,
I see that the PM8000 had it's memory bumped up in the V1.4.1 Firmware Update, but can't seem to find any official value on the Firmware PDF or any Technical Datasheets.
Do you know where I could find this information in ION Setup/PME, or in any Schneider documentation? Would be extremely useful as something to reference when discussing the meter's capabilities with customers.
Thanks in Advance,
— Scott Clysdale
Link copied. Please paste this link to share this article on your social media post.
PM8000_V001.004.001 | Download Schneider Electric
page 2: "Increased onboard log storage capacity"
Link copied. Please paste this link to share this article on your social media post.
Thanks Chen,
Is there any document that states the increased size in MB?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hey Tom,
Was able to find out using a virtual meter and ION Setup, thank you for the referral.
Official value is 342MB.