Noticed lots of ION 7300s on a PME 9.0 EMS have never logged energy.
These meters are running with firmware revision 7300V284 or 7300V277, and template 7300_FAC-4WYE_V2.2.0.0.0
These meters do not have an ION Data Recorder Module. Are any firmware revisions for the ION 7300 available that:
1. Will include a Data Recorder Module
2. Will be able to be applied to these very old meters
Link copied. Please paste this link to share this article on your social media post.
Hello Swil,
The 7300 meters do not have any version of firmware that supported onboard data recorders. Any logging for these devices will have to be in VIP. ION 7330 and ION 7350 meters did have onboard data recorders.
Charles