Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
Hi Experts,
I have a query regarding IEC61850.
The ION models have meter models that support IEC61580:
ION7650 5M logging memory
Ethernet communication
ION7550 5M logging memory
Ethernet communication
The question is, does both copper and fiber over Ethernet communication support IEC61850?
Thanks for the advise!
Regards,
Evonne
Link copied. Please paste this link to share this article on your social media post.
I think the answer is yes, both copper and fiber over ethernet communication support IEC61850.
When connecting to the Fiber port, it automatically disables the RJ45 port.
Link copied. Please paste this link to share this article on your social media post.
Thank you Khanh Trong
We want to have some opinion when we assume "Ethernet" covers for both copper and fiber supported IEC61850.
Cheers
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.