Does anyone how to wire voltage on ION8800 with the Essailec connector (see attaced)? Is there additional part required to wire voltage to the slots?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Hi Kevin,
Not sure if you got an answer already but we use a Gauge Female Slide Disconnect Terminal as shown in the image below.
Regards,
Arneil