You can also use the ION Setup Assistant, rather than go into the module level Advanced mode.
Connect to your meter using ION Setup
Open the Setup Assistant for your meter
Go to Communications > third party protocols.
In the Modbus Slave tab, select the Modbus map that you want to configure (meters ship with a Modbus map called "Default"). Click Edit to view the map.
In the viewing screen you have the option to Add values, Edit existing values, and Delete values. When you Add values you get a configuration screen that lets you define the source ION value (in your case, the I/O module outputs) the format and scaling.
Click OK to save your changes to the meter.
Link copied. Please paste this link to share this article on your social media post.
Hi Pat O'Neill,
You can use IONSetup to configure "Modbus Slave Module" ( Display in Advanced option in ION 7650 Meter ) to mapping the signals ( DI, DO ) to Modbus Register address
Please refer the guide for mapping signal to Modbus Slave Module
In Step 2: Check on "Single ION device..." and enter IP address of ION Meter
Show Advanced option in Page 4 of 9
In Step 4: You can use what area you want to mapping, Amp/Frequency...Kw/Kvar...are the default defination in ION Meter. You can rename these Area if you want
Then, you can delete Source x and Edit to "Digital In Module" or "Digital OUT module" and link to State of Sx
Then, you need pay attention to the Register Address and some properties in "Setup Register" tab ( Base Address, Format...)
Finally, Click Send to "download" configuration to IONMeter
You need to test by yourself because I just do it for mapping Electrical para before, DI and DO havve not been tested
Link copied. Please paste this link to share this article on your social media post.
Many thanks for your help
Pat O'Neill
Schneider Electric Ireland.
+353 87 252 4855
Link copied. Please paste this link to share this article on your social media post.
You can also use the ION Setup Assistant, rather than go into the module level Advanced mode.
Connect to your meter using ION Setup
Open the Setup Assistant for your meter
Go to Communications > third party protocols.
In the Modbus Slave tab, select the Modbus map that you want to configure (meters ship with a Modbus map called "Default"). Click Edit to view the map.
In the viewing screen you have the option to Add values, Edit existing values, and Delete values. When you Add values you get a configuration screen that lets you define the source ION value (in your case, the I/O module outputs) the format and scaling.
Click OK to save your changes to the meter.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.