Hi Guys
Does anyone know if is it possible to use "Harmonics Measurement Module" in ION7550 and ION7350? We required to monitor voltage and current individual harmonic angle phases. We'll be grateful if you could indicate procedure or if any firmware update is required, or indicate which type of ION can use this module to obtain these variables.
Thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
I saw the feature you need on the ION7650.
Link copied. Please paste this link to share this article on your social media post.
I believe you need 7650 for this
Link copied. Please paste this link to share this article on your social media post.
I believe James is right - PME will allow you to display whatever the device is capable of, so this is more of a hardware question. I will move your post to that community.
Tom
Link copied. Please paste this link to share this article on your social media post.
The PM8000 has the Harmonics Measurement Modules which can give both magnitude and corresponding phase angle of each individual harmonic.