Full scale or readings? about current and voltage accuracy of PM8000 and PM5000.
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2016-11-2402:47 PM
The compliance to IEC61557-12 for a particular accuracy class indicates the performance level is garunteed under a very wide range of signal conditions and various operating conditions for that parameter.
For example, Class 0.2% will be better than +/-0.2% of reading under nominal and near nominal conditions. Some allowance for de-rating is specified in the standard under more extreme conditions.