Is there any upgrade path for PM8000 and ION9000?
I'm using ION Setup 3.2.23123.01 with the following meters:
PM8000 on version 001.004.003
ION9000 on version 002.002.001
On the product web pages i have found these are the latests versions:
PM8000 004.000.000+200
ION9000 004.000.000+200
Best regards.
Link copied. Please paste this link to share this article on your social media post.
Those are the latest firmware packages. For the ION9000, you should be able to go directly to 4.0.0.
For your PM8000, your firmware is older, so I believe you will need to go to V2.1.0 first (https://www.se.com/us/en/download/document/PM8000_V002.001.000/) and from there you can subsequently upgrade to 4.0.0.
Link copied. Please paste this link to share this article on your social media post.
Those are the latest firmware packages. For the ION9000, you should be able to go directly to 4.0.0.
For your PM8000, your firmware is older, so I believe you will need to go to V2.1.0 first (https://www.se.com/us/en/download/document/PM8000_V002.001.000/) and from there you can subsequently upgrade to 4.0.0.