>>> The criteria of selection is that Diameter of toroid > 1,4 x Diameter of cables bundle
Criterias such as maximum cross section area of conductors; maximum admissible current... do not apply to Vigilohm, since we measure differential currents (these criterias only apply if the toroids are used with Vigirex devices)
NB: A version in french of this document is available here.