Hi,
Does anyone know the maximum number of Modbus TCP concurrnet connections to EGX100?
We plan to install an EGX100 to provide data to both PME7.2 and a BMS concurrently. Is there anything is should look out for or is this pretty straighforward by having the BMS contractor setup their own Modbus registers?
Regards
Edward
Link copied. Please paste this link to share this article on your social media post.
Edward,
I appreciate that this is a bit late but I believe it is 32 active connections.
Best regards,
Neil Dove
Link copied. Please paste this link to share this article on your social media post.
Thanks Neil,
We did end up doing a test just to confirm a second master could communicate with it.
Regards
Edward