Hello@SESA_B ,
I can't speak for the PM5000 series but many other devices require detecting when the signal crosses a boundary or value to determine the period of the signal then calculate the frequency from the period, without a signal, the meter cannot determine the period and therefore cannot display/determine frequency.
Can you give a screenshot showing a voltage applied to meter's measurement inputs?
Link copied. Please paste this link to share this article on your social media post.
Hi bro,
Please help me? Thanks very much
Link copied. Please paste this link to share this article on your social media post.
Hi @SESA_B I will move this to the Power Metering area for other insights. Have you brought this to Technical Support for invesitigation? If you don't get an answer here, I would suggest that as a next step.
Link copied. Please paste this link to share this article on your social media post.
What does it display when there is load on it ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi @Rich_Lannaghan ,
Yes. Load on after that appear this display.
Please help me do that.
Thanks Rich
Link copied. Please paste this link to share this article on your social media post.
Hello@SESA_B ,
I can't speak for the PM5000 series but many other devices require detecting when the signal crosses a boundary or value to determine the period of the signal then calculate the frequency from the period, without a signal, the meter cannot determine the period and therefore cannot display/determine frequency.
Can you give a screenshot showing a voltage applied to meter's measurement inputs?
Link copied. Please paste this link to share this article on your social media post.
HI @Charles_Murison ,
Thanks for your informations.
I will take a picture voltage input in this PM5350 and after that send for you consider.
Thanks very much