Hi all,
I have problem with data update rate of ION7650.
I see in display in ION7650 data update rate: 1 second, but now i want change to 1/2 cycle.
How do i do it. Can you help me? Thanks very much
If you want update rate of 1/2 cycle use HS Power Meter module.
HS Power Meter, modules update their measurement as fast as once per half-cycle (rather than
once per second). (from ION Reference)
Please see ION Reference.
Note not all modules can update at the 1/2 cycle rate, some modules are fast (1/2 cycle) some are slow (1 sec) and some are mixed where the module will update at the fastest rate connected to the inputs. Please be aware that there are some CPU loading considerations and 1/2 cycle updates take a lot more CPU usage which could cause meter to be operating at 100% and unable to add new modules or change existing.