Hi,
Recently I learnt that meters with four RS-485 terminals can form a serial string with meters that have three RS-485 terminals using Beldin 9841 or equivalent cables:
Where only Schneider meters with four RS-485 terminals exist in a serial string, what is the advantage of specifying Beldin 9842 over Beldin 9841 cables?
Would wiring a single shielded twisted pair to the D0 (-) and D1 (+), and the shield wire to the 0V (RS-485) terminal of such meters, leaving the shield terminal vacant, compromise performance in any way?
Link copied. Please paste this link to share this article on your social media post.
Would wiring a single shielded twisted pair to the D0 (-) and D1 (+), and the shield wire to the 0V (RS-485) terminal of such meters, leaving the shield terminal vacant, compromise performance in any way?
Possibly, while the shield in 4 wire connections is not connected in the meter, it does help to isolate interference. In an environment with electromagnetic interference you will see a difference in performance between the 2 configurations.
Link copied. Please paste this link to share this article on your social media post.
Would wiring a single shielded twisted pair to the D0 (-) and D1 (+), and the shield wire to the 0V (RS-485) terminal of such meters, leaving the shield terminal vacant, compromise performance in any way?
Possibly, while the shield in 4 wire connections is not connected in the meter, it does help to isolate interference. In an environment with electromagnetic interference you will see a difference in performance between the 2 configurations.