Are you looking to store the value of kVA and kVAR at the time of peak kW?
If so, could the following work for you?
Create 2 store modules, one for kVA, one for kVAR, link the inputs to the desired measurement.
Connect the kW maximum module's trigger output to store module's store input.
Link copied. Please paste this link to share this article on your social media post.
Are you looking to store the value of kVA and kVAR at the time of peak kW?
If so, could the following work for you?
Create 2 store modules, one for kVA, one for kVAR, link the inputs to the desired measurement.
Connect the kW maximum module's trigger output to store module's store input.
Link copied. Please paste this link to share this article on your social media post.
Thanks