Hi all,
We have a client possibly interested in ION9k upgrade from 8K.
I cant seem to find any Class 0.1S CT's here in Australia... given the standard is yet to be ratified, do they even exist yet, if so i would love to be sterred in the right direction.
Best Regards
Grant
Link copied. Please paste this link to share this article on your social media post.
Hi Grant,
You should look for optical CTs for 0.1S.
Areva used to have these a few years ago, but they are/were very expensive.
Regards,
Victor
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
My suggestion, in case you can't find 0.1 Class CT you may test those available CTs then put % of correction into the ITC Instrument Transformer Correction module pleas ION Reference for more detail.