Hello,
I have an inquiries from customer to use both IEC61850 (Ed2) protocol to connect to SIEMENS SCADA and ION Protocol to connect our PME for Advanced Power Quality function.
As per specification:
+) ION9000 is using Port 7700 for ION Protocol
+) And Port 102 for IEC61850.
Anyone have experience about this?
@Charles_Murison : Could you please advise?
Thank you,
Long Tran
Link copied. Please paste this link to share this article on your social media post.
Hello @LongTran ,
Yes the ION9000 meter can support ION and IEC61850 at the same time. You will need to configure the IEC61850 portion of the meter before the meter will start to talk IEC61850.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi @Charles_Murison ,
Thanks for your advise. I have well captured.