Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Posted: 2017-09-08 04:46 AM . Last Modified: 2020-12-02 03:31 AM
Link copied. Please paste this link to share this article on your social media post.
One of our client In South Africa is considering to put SagFighters @ !between the transformers and the Main LV Bus-bars. If there is already an AccuSine connected onto each of these Main LV Bus-bars, won’t these two power conditioning devices (AccuSine & SagFighter) influence each other’s operation in a bad way?
Link copied. Please paste this link to share this article on your social media post.
Hi Matlatse,
If there is already an Accusine on the system then you will have to give very careful consideration to introducing an additional source of reactance on the network. If you are using the Sagfighter to help combat the horrendous supply issues in SA, maybe consider other options, like UPSs strategically located around the site?
Link copied. Please paste this link to share this article on your social media post.
Hi Brahm, both the accusine and sagfighter are not yet connected, but the client is experiencing both sags and high harmonic@ currents, as a results of mitigating we have proposed to install a sagfighter and accusine., so we are not sure if both these units can work perfectly close to each other.