Hello everyone,
I could help with this problem that I have ?; I want to configure a ION8650B COM4 meter so you can communicate with the communication protocol DNP3.0 but shower at the time of configuration I get this error?
Deputy screenshots taken from the error.
http://www.mediafire.com/view/63j20qas0656e15/Meter_Configuration_Report_for_MW-1406A170-01.txt
http://www.mediafire.com/download/3b3hdvq50ckag94/Error+ION8650.docx
Thank You
Miguel Huaccha
Link copied. Please paste this link to share this article on your social media post.
Hi Miguel,
You have to configure the "3rd Party Protocol" for this meter via ION Setup.
In DNP3.0 option you have to set up "Connection #1" to "Communicaction port 4 (DNP V3.00)"
Best Regards
Farid