It was observed that ION 7550 MD controller to Power Logic (Schneider) SCADA values were freeze,We have reset the power supply of the meter after that analog output channel 1&2 0-20mA ports giving 36mA and this will effecting the our load shedding program.
Please advice for the solution and reason why we are getting analog output as 36 ma.
Link copied. Please paste this link to share this article on your social media post.
Hi Sanjeev,
I had a similar problem with PM8000 meter optional Input / Output card (“I/O card”) which supposed to be a bad contact issue:
I would suggest you to re-install the optional Input/Output card (“I/O card”) by following the Installing the I/O Card steps from ION7550 / ION7650 I/O Card document.
Best Regards,
Bojan
Link copied. Please paste this link to share this article on your social media post.
Sanjeev - is this resolved?
Thanks
Tom
Link copied. Please paste this link to share this article on your social media post.
I'm interested in learning more about both cases (since they have completely different designs):
1. What device or devices are in the analog loop?
what are the differential and common mode load impedances
what is the differential voltage at the analog output terminals of the =S= device
what is the voltage to earth at each of the analog output terminals of the =S= device
2. how was the 36mA DC measured? IE. value from =S= output device, clamp on DC meter, voltmeter across series load resistor, etc
3. Does powercycling the meters resolve the issue?
4. Does disconnect + reconnect the analog loop resolve the issue?
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.