Hi Experts,
PM8240 inform alarm in PME 8.1 software " DAN6 Limit Exceeded 3". So, What is the DAN6 Limit Exceeded 3. and Where I can setting value DAN6?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Help me!! Please
Link copied. Please paste this link to share this article on your social media post.
The DAN6 is referring to the "Disturbance Analyzer Module #6" which in the default framework is used for Current Swell alarm detection.
The default settings is for 155% over Current Nominal (which by default is set to 5 Amps) with a reset of 145%.
Go to the Alarm -> Sag/Swell and modify the I Swell Pickup limit or modify the Nominal current to the appropriate value.
The other number at the end probably refers to which of the 3 phases is exceeding the pickup limit (Phase A = 1, Phase B = 2, Phase C = 3) but you should check the ION Reference to be sure.
Link copied. Please paste this link to share this article on your social media post.
Hi Robert Lee,
Yes. Thanks for your information. Very helpful.
Link copied. Please paste this link to share this article on your social media post.
"DAN" I guess so that people don't have to refer to the DAM Limit?