Dears All hello,
There is a peak demand current on display of PM710. Is this peak current value monthly? or Is the maximum current value up to this day? Customer wants to see the peak current from installed on field to today.
Thanks for your support.
B&R
Ayşegül
Link copied. Please paste this link to share this article on your social media post.
Hello @AYSEGUL ,
Please note the PM700 is an old meter and no longer officially supported. The meter does have a current peak demand measurement that is the maximum current demand since the last demand reset. If customer wants this as a monthly value, the demand would need to be read at the start of each month and then reset.
You can find some information on the meter from the following links
https://www.se.com/ww/en/download/document/63230-501-207/ (Reference guide)
https://www.se.com/ww/en/download/document/63230501201A3/ (Instruction Bulletin)
https://www.se.com/ww/en/download/document/3000DB0807/ ( Quick start)
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @AYSEGUL ,
Please note the PM700 is an old meter and no longer officially supported. The meter does have a current peak demand measurement that is the maximum current demand since the last demand reset. If customer wants this as a monthly value, the demand would need to be read at the start of each month and then reset.
You can find some information on the meter from the following links
https://www.se.com/ww/en/download/document/63230-501-207/ (Reference guide)
https://www.se.com/ww/en/download/document/63230501201A3/ (Instruction Bulletin)
https://www.se.com/ww/en/download/document/3000DB0807/ ( Quick start)
Regards,
Charles