Hello @AYSEGUL ,
Just to make sure there is not confusion,. The meter supports 1 of those options at a time. You cannot have a 60Hz system and 400Hz system at the same time. You can take the meter from a 60Hz system and remove and then connect to 400Hz system.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @AYSEGUL ,
The ION76500 meters have 2 ordering options, a standard power supply (Standard power supply (85-240 V AC, ±10%/47-63 Hz / 110-300 V DC, ±10%) and a low voltage power supply (20-60 V DC))
The difference was built into the order option/Model number.
ION9000 is a lot simpler as the commercial reference determines what features the meter has. If not included in the description, the ION9000 has the standard power supply which includes the different options you mentioned already. The ION9000 also has a low Volt DC supply option as well.
METSEION92030 ION9000 meter, DIN mount, no display, hardware kit
METSEION92040 ION9000 meter, DIN mount, 192 mm display, B2B adapter, hardware kit
METSEION92043 ION9000 meter, DIN mount, 192 mm display, B2B adapter, hardware kit, Measurement Canada Ready (Canada only)
METSEION92044 ION9000 meter, DIN mount, 192 mm display, B2B adapter, hardware kit, Measurement Canada Sealed (Canada only)
METSEION92130 ION9000 Meter, 20-60 Vdc control input, DIN mount, no display, hardware kit
METSEION92140 ION9000 Meter, 20-60 Vdc control input, DIN mount, 192 mm display, B2B adapter, hardware kit
METSEION93030 ION9000 meter, LVCS, DIN mount, no display, hardware kit
METSEION93040 ION9000 meter, LVCS, DIN mount, 192 mm display, B2B adapter, hardware kit
METSEION93130 ION9000 Meter, LVCS, 20-60 Vdc control power, DIN mount, no display, hardware kit
METSEION93140 ION9000 Meter, LVCS, 20-60 Vdc control power, DIN mount, 192 mm display, B2B adapter, hardware kit
METSEION95030 ION9000T meter, HSTC, DIN mount, no display, hardware kit
METSEION95040 ION9000T meter, HSTC, DIN mount, 192 mm display, B2B adapter, hardware kit
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Dear Charles,
Thank you so much for your answer,I have just didn’t be sure the power supply of METSEION92030. Can I feed the METSEION92030 90...480 V AC 45...66 Hz +/- 10 % , 90...120 V AC 400 Hz +/- 10 % and 110...480 V DC +/- 15 %?
Thanks & Best Regards,
Ayşegül
Link copied. Please paste this link to share this article on your social media post.
Hello @AYSEGUL ,
Just to make sure there is not confusion,. The meter supports 1 of those options at a time. You cannot have a 60Hz system and 400Hz system at the same time. You can take the meter from a 60Hz system and remove and then connect to 400Hz system.
Regards,
Charles
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.