Does anybody know what the minimum voltage that the 7550RTU can take on a digital input from a pulse meter ?
The manual states external supply of maximum 130VDC but what is the minimum for the input to operate correctly ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
The ION7550 digital inputs are internally excited to -30Vdc with a high-impedance source making them most suitable for simple closed-contact sensing (zero volts).
Any (low-impedance) voltage source connected between 0V and 130V will be recognized as closed.
Hope this helps
Dan
Link copied. Please paste this link to share this article on your social media post.
Hi Richard,
Dan Loewen has provided a good description which should answer your question.
Nonetheless, here is a picture in case it is still not clear: