Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
3-phase kW and kWh calculation for BCPM
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2014-02-1709:12 PM
3-phase kW and kWh calculation for BCPM
Hi all
Presently we are trying to measure 3-phase kW and kWh using the BCPM. From the SPM software, the readings from the BCPM are only in single phase. Can we simply add all the 3-phase readings together or we need to provide a multiplication of 1.73 to the formula?
Link copied. Please paste this link to share this article on your social media post.
2014-02-1804:49 AM
Mmm. The debate will begin.
We say no, you need to choose the three phase measurement registers in the Modbus set for it to be a vector calculation, as opposed to a scalar sum you are suggesting which will be close but not right.
Early on we did find the 3 phase values to be scalar additions of the single phase measurements because PF was reading 2.75 (scalar addition of ~0.85 per phase) but I believe this was resolved to be true three phase power and power factor now.