BACnet Addons Library for Ecostruxure Machine Expert HVAC

Highlighted
Lt. Commander

BACnet Addons Library for Ecostruxure Machine Expert HVAC

I'm working on M172 controllers and need to use BACnet protocol.

 

Anybody know where can i download BACnet Addons Library for Ecostruxure Machine Expert HVAC?

7 REPLIES 7
Highlighted
Ensign

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

Hi, you can download the BACnet Addons library for ESME HVAC from this link: https://schneider-electric.box.com/s/7r58enj2e5wk3i08v37jyho5apsy445j

Please feel free to reach out for any question you might have in this regards.

Pierpaolo
----

Pierpaolo Armeli
Technical Expert Community Facilitator & HVAC Expert
Tags (1)
Highlighted
Lt. Commander

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

@Pier 

 

Thank you very much.

Tags (1)
Highlighted
Lt. Commander

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

Hi Pier,

 

I am able to discover MP172 BACnet device and objects into EBO. 

 

i have one issue about alarm and reset text Message of BI object. These are not propertied in ESME to add.

Tags (1)
Highlighted
Ensign

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

Hi,

 

the string fields can be edited only from the PLC (they are read-only)

 

You can double check on the PICS which properties are implemented (https://www.bacnetinternational.net/btl/index.php?m=266) - they are in line with the AAC profile.

 

Please contact me directly to investigate further and then we can report here the findings.

 

Thank you.

Tags (1)
Highlighted
Lt. Commander

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

I got it. Thank you.

Tags (1)
Highlighted
Ensign

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

 
Highlighted
Ensign

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

Hi Anawat,

 

As discussed, the best in this case is to use a workaround, as by using a mirror point and alarm object in EBO system.

 

Pier