Hi,
can be set, to make the modbus server respond to function 4 (read input register ) ?
Thanks.
@AmeliaFaraci : Could you help?
Rodrigo G.
Industrial Automation Community manager
Hi @Jeneburg ,
If you take a look in the page 104 of the "Modicon M251 - Logic Controller - Programming Guide" :
If I am not wrong based on the document the FC4 is not supported for Modbus TCP Server but if the client uses FC3 you can move the %IW to %MW in the controller.
I hope this helps you.
Hi @louispijpers ,
A workaround could be the use of the ADDM and READ_VAR function blocks, please find below the link to download the example:
https://schneider-electric.box.com/s/bfg5ow6frqlr0lhkhweokic0j25qqg2t
If you do not know how to import it in your project you can take a look in the next video:
https://schneider-electric.box.com/s/4bvegb89udef194mavkubonmoc6pb2of
Best regards,
Letomas
Hi Le Thomas,
Thanks, I'll give it a go.
Regards,
Louis.