Panel Downstream Transformer

In Revit, I can connect a panel upstream of a transformer, but I cannot connect another panel downstream from the transformer. What should I do?

Tags (1)

Accepted Solutions
Bowen
Crewman Crewman
Crewman

Re: Panel Downstream Transformer

the downstream panel cannot be connected to the transformer until the transformer's secondary distribution system is selected.

Please follow these steps below.

 

1. select the transformer

2. click the dropdown for Secondary Distribution System in the Properties

3. select the secondary voltage

 

Now when you try to circuit the panel, you will see the transformer as an option

 

secondary distribution system.PNG

See Answer In Context

1 Reply 1
Bowen
Crewman Crewman
Crewman

Re: Panel Downstream Transformer

the downstream panel cannot be connected to the transformer until the transformer's secondary distribution system is selected.

Please follow these steps below.

 

1. select the transformer

2. click the dropdown for Secondary Distribution System in the Properties

3. select the secondary voltage

 

Now when you try to circuit the panel, you will see the transformer as an option

 

secondary distribution system.PNG