Xenta programmable beneath an Automation Server reports "Commission failure" on download attempt

Issue

Attempting to download and commission a Xenta programmable controller beneath a SmartStruxure AS results in the following error. The application generates successfully, the application downloads successfully, but the commission step fails.

Environment

SmartStruxure Automation Server

Xenta programmable controller

Cause

There is some difference in the files generated on a save from the old Vista Menta editor, and the new SmartStruxure Menta editor.

Resolution

  1. Create the Xenta programmable device
  2. Browse in the existing Menta file
  3. Service pin the device
  4. Open the Menta file from StruxureWare Building Operation. Go to File > Save. Close the Menta file.
  5. Commission and download.
Labels (1)