Xenta Server version 5.1.5 and after Major Features

Issue

  1. Xenta Server (527/701/721/913) graphics, time schedules not working on the webpage.
  2. Xenta Server (511/555/527/913) can not create Menta object.
  3. Xenta Server (701 and 913) does not work with Xenta programmable controllers (Xenta 280/300/401).
  4. Which Xenta Server takes I/O modules and how many?
  5. Which Xenta Server works with I/NET, MicroNet, or ModBus.

Product Line

Satchwell MicroNet, TAC INET, TAC Vista

Environment

  • Xenta Server version after 5.1.5 (5.1.5 included)
  • TAC XBuilder version after 5.1.5 (5.1.5 included)
  • Vista, I/NET, LON, MicroNet, ModBus

Cause

Different Xenta Servers have different features. Using a different Xenta Server may result in missing features.

Resolution

Xenta Server 5.1.5 Major Features.

Product

LON

I/NET

MicroNet

BACNet

ModBus

Web*

I/O Modules

Xenta Supp.**

Menta Supp.

Xenta 511

X

 

 

 

X

C

 

X

 

Xenta 527

X

X

 

 

X

C

 

X

 

Xenta 527-NPR

 

X

 

 

 

S

 

 

 

Xenta 555

X

 

X

 

X

C

 

X

 

Xenta701

X

 

 

 

X

ST

10

 

X

Xenta 711

X

 

 

 

X

C

10

X

X

Xenta 721

X

 

 

 

X

ST

20

X

X

Xenta 731

X

X

X

 

X

C

20

X

X

Xenta 913***

X

X

 

X

X

S

 

 

 

*
S – Service
. Means that the web interface is automatically generated in XBuilder and only contains values in value pages and is aimed for commissioning and service.
NOTE: For Xenta 701 and Xenta 721, it is not possible to have any end-user web content, such as graphics, trend viewers, alarm viewers or value pages.  Xbuilder allows the user adding a Value Page in the Xbuilder project. It will not be displayed on the webpage though.
T – Time Object Pages. Means that Time Object Pages can be added to the XBuilder project. These will only appear for Xenta Servers 701/721 in TAC Vista Workstation and can be used to control Xenta Server time charts from Vista Workstation
C – Custom. Means that the web interface is totally configurable in XBuilder; navigation and all features for creating a full end-user web are available.

**
Xenta Supp. – Xenta 280/300/401 support. Means that Xenta 280/300/401 can be installed on the LonWorks network beneath a Xenta Server and are fully supported by both the Xenta Server and TAC Vista on top of Xenta Server.

***
The Xenta 913 also supports BacNet, M-Bus, and C-Bus.

For Xenta Server 5.1.4 major features, please read Xenta Server 5.1.4 Major Features (Xenta 5XX/7XX/913 Capabilities with Graphics, Web Applications, a....