Issue
- Xenta Server (527/701/721/913) graphics, time schedules not working on the webpage.
- Xenta Server (701) does not work with Xenta programmable controllers (Xenta 280/300/401).
- Which Xenta Server takes I/O modules and how many?
- Which Xenta Server works with I/NET, MicroNet, or ModBus.
Product Line
Satchwell MicroNet, TAC INET, TAC Vista
Environment
- Vista, I/NET, LON, MicroNet, ModBus
- Xenta Servers (Xenta 5XX/7XX/913)
Cause
Different Xenta Servers have different features. Using a different Xenta Server may result in missing features.
Resolution
Xenta Server 5.1.4 Major Features.
Product |
LON |
I/NET |
MicroNet |
BACNet |
ModBus |
Web* |
I/O Modules |
Xenta Supp.** |
Xenta 511 |
X |
|
|
|
C |
|
X |
|
Xenta 527 |
X |
X |
|
X |
C |
|
X |
|
Xenta 527-NPR |
|
X |
|
|
S |
|
|
|
Xenta 555 |
X |
|
X |
|
C |
|
X |
|
Xenta701 |
X |
|
|
|
ST |
10 |
|
|
Xenta 711 |
X |
|
|
|
C |
10 |
X |
|
Xenta 721 |
X |
|
|
|
ST |
20 |
X |
|
Xenta 731 |
X |
X |
X |
X |
C |
20 |
X |
|
Xenta 913*** |
X |
X |
|
X |
X |
S |
|
|
*
S – Service. Means that the web interface is automatically generated in XBuilder and only contains values in value pages and is aimed for commissioning and service.
NOTE: For Xenta 701 and Xenta 721, it is not possible to have any end-user web content, such as graphics, trend viewers, alarm viewers or value pages. Xbuilder allows the user adding a Value Page in the Xbuilder project. It will not be displayed on the webpage though.
T – Time Object Pages. Means that Time Object Pages can be added to the XBuilder project. These will only appear for Xenta Servers 701/721 in TAC Vista Workstation and can be used to control Xenta Server time charts from Vista Workstation
C – Custom. Means that the web interface is totally configurable in XBuilder; navigation and all features for creating a full end-user web are available.
**
Xenta Supp. – Xenta 280/300/401 support. Means that Xenta 280/300/401 can be installed on the LonWorks network beneath a Xenta Server and are fully supported by both the Xenta Server and TAC Vista on top of Xenta Server.
***
The Xenta 913 also supports BacNet, M-Bus, and C-Bus.
For Xenta Server 5.1.5 major features please read Xenta Server after version 5.1.5 (5.1.5 included) Major Features (Xenta 5XX/7XX/913 Capabilities wit....