Issue
Negative values are displaying *** asterisk instead of the value.
Product Line
TAC Vista
Environment
- XBuilder 1.6
- Vista 4
- OGC Graphics
Cause
To display negative values in XBuilder, add a placeholder for the negative value.
Resolution
In the example of terminal load, the lowest expected negative value is -100. This will require an integer value of 4 in the graphics editor in order to display -100.
If you the integer value is set to 3 and the value goes to -100, the display will show *** . This indicates the value is out of range according to the parameters set.