New in the Community? Get started here

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 
Announcements

- Who are the top users of September? Discover them here!

- Check out the ESS Active Energy Management Blog now! 

- Join us on October 23rd for a live Panel session to discuss The Power of a Sustainable Ecosystem with Hervé Coureil, Chief Digital Officer of Schneider Electric and other great speakers. Register here!

WorkPlace Tech Tool menu functions and toolbar icons do not respond when selected

Issue

WorkPlace Tech Tool menu functions and toolbar icons do not respond when selected even though they are visible (not grayed out) after changes are made to the Visio Menus or Toolbars.

Product Line

TAC IA Series

Environment

I/A Series WorkPlace Tech Tool software

Cause

Some COM add-ins are not compatible with the WorkPlace Tech Tool software.

Resolution

From the Visio menu, within WorkPlace Tech, select Tools / Customize then select the Toolbars tab. Select each checked toolbar in turn, clicking the reset button for each one. Next select the Options tab and click the "Reset menu & toolbar usage data" button.

If this does not correct the issue, disable the COM add-ins and delete the Visio directory cache using the procedure listed below. The procedure depends on the version of Visio and the version of Windows being used.

WorkPlace Tech with Visio 2007

  1. Open Visio 2007
  2. Open the Tools Pull down.
  3. Select the Options.
  4. Select the Trust Center
  5. Select Add-ins.
  6. Verify that the box "Disable all Application Add-ins" is NOT checked.
  7. At the bottom of the screen, COM Add-ins is the default selection. Press GO.
  8. In the COM Add-ins box displayed, un-check the box for the ",Send to Bluetooth", and any other third party add-ins. Click OK to apply.
  9. Close Visio 2007
  10. Delete the Visio Directory Cache file, as follows, depending on the version of Windows.
    1. If running Windows Vista or Windows 7, delete the file c:\Users\< username> \AppData\Local\Microsoft\Visio\content12.dat
    2. If running Windows XP, delete the file c:\Documents and Settings\< username> \Local Settings\Application Data\Microsoft\Visio\content12.dat
  11. Open Visio 2007 and wait for the "Getting Started with Microsoft Visio" window to be displayed.
  12. Close Visio 2007.
  13. Open WorkPlace Tech, all menu items should be there.
  14. If some or all of the WorkPlace Tech Tool menu entries are still grayed out, repeat these steps, disabling all COM add-ins.

Workplace Tech with Visio 2003

  1. Open Visio 2003
  2. Open the Tools menu.
  3. Select Options, then Security.
  4. Un-check the box for COM add-ins.
  5. Check the box for "Enable Microsoft Visual Basic for Applications".
  6. Check the box for "Enable Automation events"
  7. Click OK to apply.
  8. Close Visio 2003.
  9. Delete the Visio Directory Cache file, as follows, depending on the version of Windows.
    1. If running Windows Vista or Windows 7, delete the file c:\Users\< username> \AppData\Local\Microsoft\Visio\content.dat
    2. If running Windows XP, delete the file c:\Documents and Settings\< username> \Local Settings\Application Data\Microsoft\Visio\content.dat
  10. Open Visio 2003 and wait for the "Choose Drawing Type" window to be displayed.
  11. Close Visio 2003
  12. Open WPT, all menu items should be there.

Workplace Tech with Visio 2002

  1. Open Visio 2002
  2. Open the Tools menu.
  3. Select Options, then Advanced.
  4. Un-check the box for COM add-ins.
  5. Check the box for "Enable Microsoft Visual Basic for Applications".
  6. Check the box for "Enable Automation events"
  7. Click OK to apply.
  8. Close Visio 2002.
  9. Delete the Visio Directory Cache file, as follows, depending on the version of Windows.
    1. If running Windows Vista, delete the file c:\Users\< username> \AppData\Local\Microsoft\Visio\VISIO.BIN
    2. If running Windows XP, delete the file c:\Documents and Settings\< username> \Local Settings\Application Data\Microsoft\Visio\VISIO.BIN
  10. Open Visio 2002 and wait while Visio updates its directory cache. The process is complete when the "Choose Drawing Type" window is displayed.
  11. Close Visio 2002
  12. Open WPT, all menu items should be there.
Tags (1)
Labels (1)
No ratings