Why does "Change Inherited Attribute?" dialog box with "Cancel," "Change the value," "Break the connection," "Change the data source&...

Issue

When changing attached Template of a Personnel object from one Template to another Template, why does " Change Inherited Attribute ? " dialog box with " Cancel " , " Change the value " , " Break the connection " , " Change the data source " selections pop up?

Environment

Continuum Access / Security system with personnel template objects.

Cause

It happens only when below two conditions are met :

  1. When you change the personnel object's attached Template object to a different Template object.  
    AND  
  2. When the old Template's RefTemplate attribute value is "InheritFromTemplate" and the new Template's RefTemplate  attribute value is "CopyFrom Template".

Resolution

Change the value of RefTemplate attribute of the attached Template from "InheritFromTemplate" to "CopyFrom Template".