What protocol of the Ziton ZP3 Fire Detection System does our Xdriver utilize?

Issue

What protocol of the Ziton ZP3 Fire Detection System does our Xdriver utilize?

Environment

Continuum Xdriver - Ziton Fire Panel

Cause

Need to confirm that the XDriver is able to communicate to third party fire panel.

Resolution

The Ziton XDriver has been developed to the ZCP2 communications protocol V2.01. Contact the manufacturer to confirm whether the panel supplied supports this version of the protocol.
 

Further information on the XDriver can be found at the link below.

Clymac - Ziton Fire Panel