What is the operating environment of Continuum controllers

Issue

What is the operating temperature / humidity of Continuum controllers

Environment

Continuum

B3xxx

i2xxx

IO module

ACX52xx

ACX54xx

CX9xxx

Cause

The operating Environment for the Continuum controller range

Resolution

The operating Environment for the Continuum controller range is as follows:

 

Temperature

32°-120°F (0-49°C)

 

Humidity

10-95% RH (non-condensing)

This is the maximum Temperature and Humidity within the controller(s) enclosure, if the room is at 49°C then the temperature within the enclosure may be much warmer.