What is the longest time delay that can be used for relay modules within MR controllers?

Issue

What is the longest time delay that can be used for relay modules within MR controllers?

Environment

  • I/NET MR controllers
  • DDC Relay modules

Cause

Limitations within the controller and programming.

Resolution

3299 seconds is the longest configurable delay. That equates to 54 minutes, 59 seconds.