Issue

Is it possible to configure the On/Off output as a PWM output?

Environment

Viconics

SE7200

SE7200C5545W

Cause

In some applications its desirable that the output is configured as PWM.

Resolution

The main On-Off outputs cannot be set as PWM, they go up to 8 CPH.

However, the BO5 output can be On/Off (4 CPH) or PWM (10sec. cycles).