Various errors are reported when attempting to edit the station database in a I/A Series R2 UNC.

Issue

Engineer is using his I/A Series R2 notebook to edit customer's UNC station.

Getting errors in Standard Output Window regarding out of data modules and missing modules.

Environment

I/A Series R2 WPP and UNC.

Cause

Engineer's copy of WPP does not have the same version of the I/A Series R2 software or some of the modules are not of the same revision.  UNC station was originally edited from the Enterprise Server on the site.

Resolution

  1. Insure the version of all modules used in the UNC match those installed in the nre\modules folder of the WPP system.
  2. Insure that the version of the NiagaraD service being run on the computer matches the version of software installed in the UNC.
Tags (2)