Using Absolute and nviEffectiveStpt together on a STR-350

Issue

In some situations, the STR-350 is needed to send an absolute setpoint to another device on the network, and the nviEffectiveStpt is needed to be able to raise or lower that setpoint over the network. When doing this, the nvoSetpoint will not mirror the set value in the nviEffectiveStpt. 

Environment

STR-350 v1.2 & v1.3

Cause

If the nciSendHeartbeat is greater than 0, the stat will only use the adjusted value at the stat and will ignore a network value from the nvi. 

Resolution

Set the nciSendHeartbeat to and any change on the nviEffectiveStpt will be reflected on the nvoSetpoint and as the current setpoint on the stat.