Upgrading to Niagara G3 3.8 causes the PxIncludes to not fully render and the graphics are slow to load.

Issue

After upgrading to Niagara G3 3.8 (from 3.7), nested PxIncludes now only partially load and very slowly.  They are not all entirely missing.  After a screen refresh, most will load except for a random few.  Also, they may load all at one moment but not the next.  The same Px file in version 3.7 loads faster with nothing missing.

Environment

Niagara G3 / AX version 3.8

Cause

PxInclude caching is disabled by default in 3.8.

Resolution

This issue was addressed with the release of an updated bajaui module - version 3.8.38.3.  This version re-enables PxInclude caching.  Download it here.