Unwanted 'Pan and Zoom' on TGML Graphics when using Webstation

Issue

When editing an EBO graphic in Webstation rather than Workstation, there is an inherent feature which allows a user to zoom in and out of the graphic using the mouse scroll. They can also pan around the page by holding down the left mouse button as they move.

In many cases however, this feature is not wanted and makes the graphic more difficult to use.

Image Zoomed Out 

zoom_out.png

Image Zoomed In and Panned Right

zoom_in.png

Product Line

Building Operation Webstation

Environment

  • Graphics

Cause

Pan and Zoom in Webstation are features that are enabled by default in all TGML Graphics

Resolution

Edit the graphic object and select the top TGML root of the page properties. There is a 'Disable Pan and Zoom' option which by default is set to False.  Setting this option to True and then saving turns off the Pan and Zoom functions for that graphic