Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Unable to transfer values from third party device in a Cyberstation Program.

Issue

A Cyberstation program will not transfer the value of an AnalogValue in a third party device to an AnalogValue point in Continuum.

The Cyberstation program consistently errors out and disables.

Environment

  • Point Transfer
  • BACnet

Cause

Using a Cyberstation program to set the value of a point in a BCX controller to equal the value of a point in a third party device without an intermediate step.

Resolution

  1. Create AnalogValues in the Cyberstation. 
  2. Point values should first be transferred from the third party device to the Cyberstation points.
Tags (1)
Labels (1)