Unable to set up Report - Chart object in Vista

Issue

Although a new Report - Chart object can be created in Vista, there is no documentation that explains how to make it work or what it does

Environment

TAC Vista 4.2.0 Workstation and newer

Cause

The Report - Chart function was removed in Vista 4.2.0 although it can still be created up through Vista 5.1.8

Resolution

Although it was possible to create a new Report - Chart object in Vista 4.2.0 - Vista 5.1.8, the objects were not functional. The Report - Chart object was replaced with the Trend Chart object and instructions on how to set up Trend Chart objects can be found in the Vista documentation.